dradam
Well-Known Member
- Thread starter
- #61
Super helpful! I plan to use 1" flex pvc for 3x 6awg and a ground Likely 8 AWG. One will be an unused neutral which will not be live unless needed in the future. This should far exceed minimum requirements.Just need to review the allowable conduit fill charts based upon the type of conduit you plan to use so there is sufficient air space around the wires for cooling. The wiring charts are either based on the wires in free air which allow them to get a bit warmer and be naturally cooled and carry more current or wires encased in conduit or enclosure that takes into account that conduit is going to get warm as the wires naturally warm carrying current and not allow the wires to cool as much as if they were on a pole in the air.
So the conduit fill charts are as important as the wire sizes them selves
hope that helps
Thank you again.