Wall charger wire gauge question
R1S88
Massachusetts
I'm having a Rivian Wall Charger installed in the garage of a high rise apartment building. It's quite a long run and the electrician wants to run copper 4 awg wire to reduce voltage drop. Question - will he have to drop it down to 6 awg near the charger in order to fit the terminals of the Rivian Wall Charger? Or, can the 4 awg work? Thanks,
Polar
C40, LE CY R1S
He’ll have to drop it down.
Just curious how long is the run?
Running 6 and limiting to 40A might be an option to consider as well, depending on how that changes the cost.
R1S88
Massachusetts
Thanks for the response - I'm only trying to maximize charging speed and not worrying about cost. Correct me if I'm wrong, but this would not allow charging at the full capability.
Your electrician isn't wrong, he's doing the right thing by considering voltage drop. But in your case it's not significant. #6 at 1.42% voltage drop is still well under NEC maximum of 3%. Considering that #4 costs more and if done right, he needs provide approved transition from #4 to #6 which will also add to the cost.
I would measure the line voltage at the panel. It may be higher or lower than than 240v. I'd just go with #6 as long as the line voltage is at least 238 volts at the panel.
Rivian R1T R1S Wall charger wire gauge question 1774636449332-eh
R1S88
Massachusetts
very helpful - thanks
beatle
Springfield, VA
I did 50ft 6awg Romex for my first Tesla UWC since it was run in-wall. I did 8awg in conduit to the second one about 15 feet away. These share a 50A breaker and are set at 40A charge speed. 4awg is definitely not necessary.
RivianRiverRat
Greg
Chattanooga TN
2022 Rivian R1T
Civil Engineer
Are you in a jurisdiction that requires a permit and inspection for the work?
If so check with them on code requirements
Eeyore
Bruce
Retired Union Electrician
I agree with this response. Well done.
Time2Roll
2026 R1S Quad - 2001 F150
I agree with #6. Going oversize does nothing except add unneeded cost and two more connections that could have issues.
Supratachophobia
Ohio
S
About 80 feet
I don't think that's too far to be honest. I'm pushing 2 Tesla HPWC and their runs are 60 and 75ft respectively. Both have 6-3 with the longer run going on 12 years or so.
You can always run the 4 gauge to a disconnect or sub panel right before the charger and then drop to 6-2 at the breaker or disconnect.
R1S88
Massachusetts
Update: I was given a more accurate measurement and it’s actually 130 feet. I suspect the answer is still to go with 6 awg, but thought I would ask the experts here to be sure. Thanks!