IIRC, it's against NEC to bond ground and neutral at any point outside of the main load center. Even sub-panels must keep their ground and neutral separate.
The reason for this is to avoid ground loops. If you provide an alternate path for ground to hit neutral, you're going to get energy flowing in weird directions, and stuff that has the circuit switched off might have energy potential.
Sponsored

 
OP
OP
lefkonj

lefkonj

Well-Known Member
First Name
Jeff
Joined
Feb 6, 2021
Threads
37
Messages
1,450
Reaction score
2,618
Location
New Jersey
Vehicles
Gen2 R1S Tri, I4-m50
Clubs
 
I have a quick question about this. The R1T will be our 1st EV. I have currently preordered the Rivian charger and was thinking I'd coordinate the install as part of the delivery process. Am I making a mistake? if yes - what would be a recommended path to take? thanks for your input.
Don't wait. The port is a standard connection for the Rivian charger, wall box, ElectrifyAmerica and the list goes on. If the electricians need weeks to get to your place you wouldn't want the vehicle and charger but have to wait for the port for another 2 months.
 

ajdelange

Well-Known Member
First Name
A. J.
Joined
Aug 1, 2019
Threads
9
Messages
2,883
Reaction score
2,319
Location
Virginia/Quebec
Vehicles
Tesla XLR+2019, Lexus, Landcruiser, R1T
Occupation
EE Retired
IIRC, it's against NEC to bond ground and neutral at any point outside of the main load center. Even sub-panels must keep their ground and neutral separate.
That is essentially correct with the correction being that the neutral and ground must be bonded at the service entrance and only at the service entrance. If the main load center is the service entrance, as it often is, that is the only place where the bond is allowed. The "bonding screw" must be removed in a sub panel.
 

ajdelange

Well-Known Member
First Name
A. J.
Joined
Aug 1, 2019
Threads
9
Messages
2,883
Reaction score
2,319
Location
Virginia/Quebec
Vehicles
Tesla XLR+2019, Lexus, Landcruiser, R1T
Occupation
EE Retired
The reason for this is to avoid ground loops. If you provide an alternate path for ground to hit neutral, you're going to get energy flowing in weird directions, and stuff that has the circuit switched off might have energy potential.
The reason is to prevent "objectionable current" from flowing in the earthing conductor. The neutral carries all the imbalance currrent and thus at distal points in the system is at higher potential than ground (from the current induced voltage drop). If it is bonded to the earthing conductor anywhere other than at the service entrance the grounding conductor will carry some of the imbalance current and also be at higher potential as will the metal parts of anything connected to that grounding conductor.
 
Last edited:

sub

Well-Known Member
Joined
Jul 23, 2021
Threads
34
Messages
1,873
Reaction score
3,306
Location
USA
Vehicles
Rivian R1S, Tesla Model 3
I have a quick question about this. The R1T will be our 1st EV. I have currently preordered the Rivian charger and was thinking I'd coordinate the install as part of the delivery process. Am I making a mistake? if yes - what would be a recommended path to take? thanks for your input.
I would assume that Rivian is not going to give you an exact time/day with much advance notice. Unless the electrician is a good friend who can come over on a moment's notice, arranging to have an electrician show up immediately after the car arrives would be difficult.

I would go ahead and have an electrician install a 14-50 plug in your garage. That way you are all set to plug your car in the moment it arrives.

If you have the electrician use wire rated for 60A (1 size thicker than they would normally use for a 14-50 plug), once the wall charger arrives, installing it will be a 10 minute job. All they will have to do is replace the 50A breaker with a 60A breaker and then attach the wall charger where the 14-50 was. And you won't be in a rush because you can charge using the 14-50 until the electrician is able to come out and install the wall charger.

The wall charger can most likely be installed on 50A wire, but your max charging rate would be limited to 40A instead of the 48A you would get with a 60A circuit. Max charging rate will be 80% of circuit's nominal rating.
 
Last edited:

Sponsored

Dark-Fx

Well-Known Member
First Name
Brian
Joined
Jul 15, 2020
Threads
148
Messages
13,592
Reaction score
27,464
Location
Michigan
Vehicles
R1T, R1S, Livewire One, Sierra EV, R1S
Occupation
Engineering
Clubs
 
I have a quick question about this. The R1T will be our 1st EV. I have currently preordered the Rivian charger and was thinking I'd coordinate the install as part of the delivery process. Am I making a mistake? if yes - what would be a recommended path to take? thanks for your input.
Charging off of a 120V circuit should still get you ~1.5-2 miles of range an hour. If you're not going to drive your vehicle more than 20-25 miles a day you can probably survive off it for a while.
 

ajdelange

Well-Known Member
First Name
A. J.
Joined
Aug 1, 2019
Threads
9
Messages
2,883
Reaction score
2,319
Location
Virginia/Quebec
Vehicles
Tesla XLR+2019, Lexus, Landcruiser, R1T
Occupation
EE Retired
I have a quick question about this. The R1T will be our 1st EV. I have currently preordered the Rivian charger and was thinking I'd coordinate the install as part of the delivery process. Am I making a mistake? if yes - what would be a recommended path to take? thanks for your input.
You might want to get an electrician in now and tell him what you are planning to do so he can get you on his schedule ASAP. These trucks are supposedly really rolling out next month. Find an electrician that has done EVSE installs before. It would be nice if Rivian made the installation manual for the charger available now but installation of any of them is pretty straight forward.

One thing I would do is tell the man you want him to pull 6/3 even though the neutral will not be used. This is because you do not know that at some future date you might not want to replace that EVSE with something else that requires the neutral such as a 14-50R receptacle. Copper, of course, isn't cheap but even so the marginal cost of that 4th conductor should be small.
 

Jamuso

Well-Known Member
First Name
Joe
Joined
Jul 9, 2021
Threads
0
Messages
272
Reaction score
347
Location
CT
Vehicles
Ridgeline
Occupation
Sr software engineer - manager

Gearhead500

Well-Known Member
First Name
John
Joined
Dec 10, 2020
Threads
11
Messages
248
Reaction score
481
Location
Phoenixville
Vehicles
Ford F-150 XLT
Occupation
Director of Marketing & Ecommerce
Might I suggest some nice cut to length 6/3 SOOW from a solid company. We, I mean, “they” have millions of feet nationwide in 24 distribution centers and Canada.

Now if you want a metal clad jacket or some tray cable that is rated for direct burial…”They” also have some direct burial that has a gopher resistance jacket.

???
Their marketing guy seems awesome.

https://www.omnicable.com/products/...and-portable-cord-flexible-and-portable-cord/
 

DucRider

Well-Known Member
First Name
Gary
Joined
Oct 21, 2019
Threads
17
Messages
1,691
Reaction score
3,188
Location
ORegon
Vehicles
Polestar 2, Ioniq, R1S
For those looking to pre-wire, no need to install an outlet/port at all. Just getting the 6/2 or 6/3 wires pulled
Might I suggest some nice cut to length 6/3 SOOW from a solid company. We, I mean, “they” have millions of feet nationwide in 24 distribution centers and Canada.

Now if you want a metal clad jacket or some tray cable that is rated for direct burial…”They” also have some direct burial that has a gopher resistance jacket.

???
Their marketing guy seems awesome.

https://www.omnicable.com/products/...and-portable-cord-flexible-and-portable-cord/
What jurisdiction allows SOOW for running circuits in a home?
 

Sponsored

MIG

Well-Known Member
Joined
Apr 9, 2021
Threads
26
Messages
470
Reaction score
695
Location
Chicago
Vehicles
Prius; R1S
We've been househunting and one of the homes we walked through had a newly-updated garage with great lighting, a freshly-epoxied floor and dual level 2 chargers. I loved it but apparently my wife wasn't happy with the other rooms.
 

Gearhead500

Well-Known Member
First Name
John
Joined
Dec 10, 2020
Threads
11
Messages
248
Reaction score
481
Location
Phoenixville
Vehicles
Ford F-150 XLT
Occupation
Director of Marketing & Ecommerce
For those looking to pre-wire, no need to install an outlet/port at all. Just getting the 6/2 or 6/3 wires pulled

What jurisdiction allows SOOW for running circuits in a home?
To a mobile home?
I was being sarcastic. Sorry.
SOOW isnt rated for indoors. You should use NM, THHN, or Armored cable if your local ordnance is reeeeeeeally strict. It def depends on if needs to be rated for wet locations or if your install calls for direct burial which NM aka Romex (most of Lowe’s/Home Depot) is not rated for either. A good tray cable is overkill but the most flexible as it is rated for direct burial, sunlight resistant, hanging, exposed runs…. I’ll stop nerding out on cable, types of jackets, and applications.
 

nfrank

Well-Known Member
First Name
Nathan
Joined
Sep 30, 2019
Threads
16
Messages
359
Reaction score
528
Location
Bay Area, CA
Vehicles
F-150
To a mobile home?
I was being sarcastic. Sorry.
SOOW isnt rated for indoors. You should use NM, THHN, or Armored cable if your local ordnance is reeeeeeeally strict. It def depends on if needs to be rated for wet locations or if your install calls for direct burial which NM aka Romex (most of Lowe’s/Home Depot) is not rated for either. A good tray cable is overkill but the most flexible as it is rated for direct burial, sunlight resistant, hanging, exposed runs…. I’ll stop nerding out on cable, types of jackets, and applications.
Ok, cable nerd, what are your thoughts on building your own ev charger? I'd really like a cable that's over 25ft long. Something like 45ft long. I have never seen an ev charger over 25ft so I'm assuming there's some sort of regulation.
 

Gearhead500

Well-Known Member
First Name
John
Joined
Dec 10, 2020
Threads
11
Messages
248
Reaction score
481
Location
Phoenixville
Vehicles
Ford F-150 XLT
Occupation
Director of Marketing & Ecommerce
Ok, cable nerd, what are your thoughts on building your own ev charger? I'd really like a cable that's over 25ft long. Something like 45ft long. I have never seen an ev charger over 25ft so I'm assuming there's some sort of regulation.
I plan Tray cable because I have access to it, but like I said it is 100% about your local ordinance and how it is run. THHN in a conduit is what most electrician would do IMO
EDIT I didn’t realize Romex has a THHN jacket. Sorry we don’t stock that. So Romex in a conduit and 45’ shouldn’t be an issue
 
Last edited:

DucRider

Well-Known Member
First Name
Gary
Joined
Oct 21, 2019
Threads
17
Messages
1,691
Reaction score
3,188
Location
ORegon
Vehicles
Polestar 2, Ioniq, R1S
Ok, cable nerd, what are your thoughts on building your own ev charger? I'd really like a cable that's over 25ft long. Something like 45ft long. I have never seen an ev charger over 25ft so I'm assuming there's some sort of regulation.
NEC 625.17