Well-Known Member
@pcrampton, you have 2 slots available in your panel - slots 22 and 24. Based off your existing circuit breakers, you could add a double-pole (240 Volt) circuit breaker in these slots. It would be like the ones you have installed in 3/5, 4/6, 7/9, 8/10, and 11/13. I've actually surprised that you have so many 240V circuits already, unless you have electric heat for the house and/or water.
While the new circuit breaker would physically fit, you (or the electrician) still need(s) to do a load calculation to see how large of a circuit you could install in that spot. Depending upon the currently installed items, you may not be able to legally put a 50 or 60 amp circuit breaker in there. You may end up and be limited to a lower amperage.
While the new circuit breaker would physically fit, you (or the electrician) still need(s) to do a load calculation to see how large of a circuit you could install in that spot. Depending upon the currently installed items, you may not be able to legally put a 50 or 60 amp circuit breaker in there. You may end up and be limited to a lower amperage.