Just to be clear, an EVSE is always considered a continuous load and the circuit needs to be sized accordingly. There is no exception for shorter charge times.Max continuous (>2 hours) is 80% of the circuit rating, thus 40A limit for 50A circuit and 48A limit for 60A circuit.