Charging before Wall Charger Delivered

LaunchGreen

Well-Known Member
Joined
Apr 10, 2021
Threads
5
Messages
524
Reaction score
1,105
Location
California
Vehicles
Range Rover
Not going to help you, but maybe others; I had the wiring run a couple of months ago. The electrician put in a 14-50 and left me with extra cable and instructions to remove the plug and direct wire the Rivian charger myself.
Sponsored

 

SANZC02

Well-Known Member
First Name
Bob
Joined
Feb 11, 2021
Threads
30
Messages
5,329
Reaction score
8,984
Location
California
Vehicles
Tesla Model S, LE - R1S
Occupation
Retired
Without knowing how much you drive each day hard to give a detailed solution. One of the simplest is find a DCFC charger near you and drive by there to top off.

If you drive 40 miles a day and stop by a DCFC charger for 15 or 20 minutes every other day or so it will bridge the gap until you get your charger. I have a Tesla with free super charging and sometimes go months at a time without charging at home.
 

Rhidan

Well-Known Member
Joined
Nov 25, 2020
Threads
9
Messages
585
Reaction score
1,505
Location
Denver
Vehicles
R1T
I'm in the same boat. Signed up for the Xcel program and reached out to an electrician in March, but R1T is going to beat the electrician to my garage. Electrician told me last night that they are all out of chargepoint flex EVSEs (which are necessary to get the off-peak program through Xcel) and no clue when they will be back in stock. I also ordered the Rivian EVSE, but that's for a mountain home and I told Rivian to prioritize getting the EVSE to other owners first who need it in their garage. Not expecting the Rivian EVSE until later this summer.

I'm seeing if the electrician can install a 14-50 NEMA in my garage for the time being, but it still looks like the earliest appointment will be first week of June.

There's a 6kW chargepoint in my parking garage at work. Looks like I'm going to be using some combination of the standard wall outlet, L2 at work, and L3 when needed to make things work for the first few weeks of ownership. Rivian said this was going to be an "Adventure," after all.
 

Jamuso

Well-Known Member
First Name
Joe
Joined
Jul 9, 2021
Threads
0
Messages
251
Reaction score
330
Location
CT
Vehicles
Ridgeline
Occupation
Sr software engineer - manager
We have a seasonal campsite near us with a 30amp connection. I'm planning on getting the 30amp to 240 amp adapter from amazon and will be using that to charge between delivery and charger install.
 

CommodoreAmiga

Well-Known Member
Joined
Dec 30, 2020
Threads
39
Messages
4,104
Reaction score
7,712
Location
INACTIVE
Vehicles
INACTIVE
While it would work (with a DIY hack that puts a 14-50 outlet on a 30 amp circuit), it certainly would not be legal/code compliant.
What code does it violate?
 

Sponsored

timesinks

Well-Known Member
Joined
Sep 20, 2020
Threads
6
Messages
570
Reaction score
1,851
Location
Seattle
Vehicles
R1T, ID.4, Sprinter
What code does it violate?
For starters, NEC 110.3(B), which is apparently the most-cited correction inspectors make here in WA:
Installation and Use. Equipment that is listed, labeled, or both shall be installed and used in accordance with any instructions included in the listing or labeling.
And, from the instructions for the portable charger:
  • Don't attempt to attach Portable Charger adapters to electrical outlets not listed in this guide.
  • Don't plug the Portable Charger adapter into an extension cord, power converter, power strip, or any type of power adapter.
So it is a violation of code. Is it unsafe? I'd say not if the max rate is appropriately configured.

And just to fully acknowledge the pedantry here, it's also technically a code violation to use the charger with any other EV, because:
  • The Portable Charger works with Rivian vehicles only. Don't use the Portable Charger for any other purpose or to charge any other vehicle.
A close reading of NEC Article 625 can probably uncover some additional technical violations.

Does it matter? No, not really. Is it a code violation? You betcha.
 

sub

Well-Known Member
Joined
Jul 23, 2021
Threads
23
Messages
1,411
Reaction score
2,426
Location
USA
Vehicles
Rivian R1S, Tesla Model 3
What code does it violate?
I don't have a copy of the code in front of me to cite the exact paragraph, but are you really doubting that it is against the code to install a 50 amp outlet on a 30 amp circuit? It doesn't matter what you plan to plug into the outlet, you can't put a 50 amp outlet on a 30 amp circuit and be compliant.

And in addition to the amperage difference, many dryer outlets are 10-30's which do not have a ground wire. Although you could connect the 14-50's ground and neutral pins to the 10-30's neutral pin and it would work, that too is just obviously non-compliant.
 
Last edited:

Birdowin

Well-Known Member
First Name
Matt
Joined
Mar 14, 2022
Threads
13
Messages
161
Reaction score
130
Location
Portland OR
Vehicles
Rivian R1T / Tesla model S
Occupation
Retired from construction.
Looks like my RT1 will be delivered on Saturday, but no clue on when I will get the wall charger. It sounds like my best option will be charging off my dryer outlet. I assume others have ran into the same problem? Did you use an extension cord? It looks like the provided length is only 4 feet....
Our Tesla charges on a NEMA 14-50 outlet on a 50 amp circuit. As far as I can tell this gets you the same charge rate as the Rivian wall charger. I think that is the most charge that you can get out of a 240v electric panel. Our 2014 Tesla charges at about 30mph on this system. I would hope that the Rivian comes with a NEMA 14-50 adapter.
 
OP
OP
bdavis171

bdavis171

Well-Known Member
First Name
Brandon
Joined
Mar 14, 2022
Threads
9
Messages
117
Reaction score
119
Location
Minneapolis
Vehicles
Rivian R1T
Since my wall charger circuit is already wired at 60 amp, putting in a temporary solution on that wouldn't quite work without buying a charger as well. Ended up buying the 30amp charger from Amazon to run off my dryer outlet until my long term solution arrives. I will report back next week on how well that works
 

timesinks

Well-Known Member
Joined
Sep 20, 2020
Threads
6
Messages
570
Reaction score
1,851
Location
Seattle
Vehicles
R1T, ID.4, Sprinter
Our Tesla charges on a NEMA 14-50 outlet on a 50 amp circuit. As far as I can tell this gets you the same charge rate as the Rivian wall charger. I think that is the most charge that you can get out of a 240v electric panel. Our 2014 Tesla charges at about 30mph on this system. I would hope that the Rivian comes with a NEMA 14-50 adapter.
The portable charger will max out at 32A because it's code-compliant to put a NEMA 14-50R on a 40A circuit and EVSEs require de-rating to 80%. It does have a NEMA 14-50P dongle.

The wall charger goes on a 60A circuit and can max out at 48A.

The same amount of energy will propel a Rivian fewer miles than a Tesla because the Rivians are heavier and not shaped like eggs. You'll probably see something closer to 16 miles-of-range-per-hour-of-charge at 32A and about 24 miles-of-range-per-hour-of-charge at 48A.
 

Sponsored

Lsthrz

Well-Known Member
First Name
David
Joined
Mar 13, 2022
Threads
10
Messages
168
Reaction score
319
Location
Colorado
Vehicles
2017 Tesla S, 2012 LR4
Occupation
Geologist
You most likely can't use the included charger on your dryer outlet. Dryer outlets are generally only 30 amps and the included charger requires at least a 40 amp circuit.

If you can find a used Telsa mobile charger and a Tesla adapter, you can use that on a dryer circuit with the right pigtail.

There are probably other chargers that work on 30 amp circuits, but the Tesla is the only one I know.
I have charged without issue off a 30a outlet with the included Rivian charger (not the Wall Charger) . Just had to use an adapter to connect the cable but no issues with charging.
 

Birdowin

Well-Known Member
First Name
Matt
Joined
Mar 14, 2022
Threads
13
Messages
161
Reaction score
130
Location
Portland OR
Vehicles
Rivian R1T / Tesla model S
Occupation
Retired from construction.
The portable charger will max out at 32A because it's code-compliant to put a NEMA 14-50R on a 40A circuit and EVSEs require de-rating to 80%. It does have a NEMA 14-50P dongle.

The wall charger goes on a 60A circuit and can max out at 48A.

The same amount of energy will propel a Rivian fewer miles than a Tesla because the Rivians are heavier and not shaped like eggs. You'll probably see something closer to 16 miles-of-range-per-hour-of-charge at 32A and about 24 miles-of-range-per-hour-of-charge at 48A.
Thanks for that. In Oregon at least you can install a NEMA 14-50 on a 50 amp breaker. Ours was done by an electrician and inspected by the city. But our Tesla only draws 40Amps max.
I talked to one of the tech people at Rivian and they told me either the Rivian charger or the NEMA 14-50 on a 50A circuit would give the same amount of charge but I'm not really sure that they really knew what they were talking about.
 
OP
OP
bdavis171

bdavis171

Well-Known Member
First Name
Brandon
Joined
Mar 14, 2022
Threads
9
Messages
117
Reaction score
119
Location
Minneapolis
Vehicles
Rivian R1T
For anyone else curious, I have been using this to charge temporarily from my dryer. Works great!

 

ajdelange

Well-Known Member
First Name
A. J.
Joined
Aug 1, 2019
Threads
9
Messages
2,883
Reaction score
2,317
Location
Virginia/Quebec
Vehicles
Tesla XLR+2019, Lexus, Landcruiser, R1T
Occupation
EE Retired
I talked to one of the tech people at Rivian and they told me either the Rivian charger or the NEMA 14-50 on a 50A circuit would give the same amount of charge but I'm not really sure that they really knew what they were talking about.
The device that comes with the truck plugged into a 14-50R delivers 32A. The Rivian wall charger hard wired to a 50A circuit would deliver 40A. The wall charger equipped with a 14-50R pigtail is not really kosher but to get it as compliant as possible one would program it for 40A if he knew the receptacle it was plugging into was on a 50A circuit;
 

pc500

Well-Known Member
Joined
Jun 22, 2021
Threads
19
Messages
1,019
Reaction score
550
Location
US
Vehicles
dodge ram
I don't have a copy of the code in front of me to cite the exact paragraph, but are you really doubting that it is against the code to install a 50 amp outlet on a 30 amp circuit? It doesn't matter what you plan to plug into the outlet, you can't put a 50 amp outlet on a 30 amp circuit and be compliant.

And in addition to the amperage difference, many dryer outlets are 10-30's which do not have a ground wire. Although you could connect the 14-50's ground and neutral pins to the 10-30's neutral pin and it would work, that too is just obviously non-compliant.
There is actually lots of code lateral allowances for circuit breakers being less than plugs at 240v.