Sponsored

Low voltage on a 208v EVSE, problem?

KootenayEV

Well-Known Member
First Name
Andrew
Joined
Sep 22, 2021
Threads
18
Messages
375
Reaction score
308
Location
Nelson, BC
Vehicles
R1T, Tesla Model 3
Occupation
Environmental Engineer
I'm sitting at a public EVSE at a visitor centre which is likely a 208v power supply. Truck is reporting 48A being drawn off a Clipper Creek unit, and my truck is showing 9.1kW. Doing the math on that yields voltage of 189v. That seems like a really large voltage drop, over 9%. I've used this charger before with no ill effects, but hadn't noticed the implied voltage. (Side note: I like that my Model 3 report both voltage and amps, then it's really obvious.)

Question: will the onboard charger handle any voltage between about +-10% of the nominal voltage range it claims to work in? (e.g. 120-240v; equaling ~108v to 264v.) Or is there a discrete step range in between 120 and 240 where it doesn't like to function?
Sponsored

 

pc500

Well-Known Member
Joined
Jun 22, 2021
Threads
20
Messages
1,021
Reaction score
550
Location
US
Vehicles
dodge ram
I don't know but unless the rivian is reporting actual voltage I wouldn't trust computations based on amperage much. Sometimes those numbers can lie for example it might be telling you the amount into the battery and not lost due to efficiency.
 

Dark-Fx

Well-Known Member
First Name
Brian
Joined
Jul 15, 2020
Threads
98
Messages
9,636
Reaction score
18,423
Location
Michigan
Vehicles
Polestar 2, R1T, R1S, Livewire One, Fisker Ocean
Occupation
Engineering
Clubs
 
Back when I was doing some testing, I could still get the polestar and Rivian to pull 48A on a circuit the polestar was registering as 107V after voltage drop. No complaints from either vehicle about the voltage being low
 

Cosmacelf

Well-Known Member
Joined
Nov 11, 2020
Threads
18
Messages
420
Reaction score
510
Location
San Diego, CA
Vehicles
Rivian R1S, Tesla Model X
Occupation
Software
The car's charger has to boost whatever voltage it gets to around 350V pack voltage, and certainly it can accept 120V, so there is no reason for it to complain about 192V. And yes, I can absolutely believe the voltage sag is that bad. That 208V circuit is probably very long back to the panel, and I'd bet they didn't upsize the wire for that long run, resulting in lots of losses along the wire at 48A.
 

Zoidz

Well-Known Member
First Name
Gil
Joined
Feb 28, 2021
Threads
108
Messages
3,206
Reaction score
7,050
Location
PA
Vehicles
23 R1S Adv, Avalanche, BMWs-X3,330cic,K1200RS bike
Occupation
Engineer
As mentioned above, you are assuming that the supply is 208 volts to the charger. You don’t know that. NEC allows a 3% voltage drop on a branch circuit, so it could be 202 volts. The utility may not be providing 208 volts. It’s not uncommon for the utility voltage to fluctuate throughout the day. There are losses through all of the circuitry all the way to the battery. It’s really of no value to try to reverse analyze this. If the vehicle says it is charging…… it is.
 
OP
OP
KootenayEV

KootenayEV

Well-Known Member
First Name
Andrew
Joined
Sep 22, 2021
Threads
18
Messages
375
Reaction score
308
Location
Nelson, BC
Vehicles
R1T, Tesla Model 3
Occupation
Environmental Engineer
Thanks for the replies - totally allayed my curiosity. Cheers.