PSA - reminder for everyone to do a check-up on your EVSE infrastructure if you've got it at your house.

Some of you will recall I had Mr Melty (electrician used a residential-grade NEMA 14-50 the first time. which subsequently melted in the wall), and the concerns put out by Munroe et. al. regarding breakers frying because of loose connectors or not being rated for continuous 40+ amp draw.

So - 3 nights ago, the breaker on my EVSE blew immediately after the charge schedule initiated at midnight. In the morning, I tried again - blew within 5 minutes. I didn't have time to debug leading up to NYE so I just charged at public infrastructure until today.

Took a look at the breaker, and the lugs were absolutely loosened up, presumably from heat cycles and time. A quick crank-down and it's been running at full-tilt for the last 30 minutes.

TL;DR - do a once/year checkup on your electrical connections for your EVSE so nothing gets melty.
Sponsored

 

godfodder0901

Well-Known Member
First Name
Jared
Joined
Mar 12, 2019
Threads
27
Messages
5,767
Reaction score
10,158
Location
Washington
Vehicles
2022 Rivian R1T LE
PSA - reminder for everyone to do a check-up on your EVSE infrastructure if you've got it at your house.

Some of you will recall I had Mr Melty (electrician used a residential-grade NEMA 14-50 the first time. which subsequently melted in the wall), and the concerns put out by Munroe et. al. regarding breakers frying because of loose connectors or not being rated for continuous 40+ amp draw.

So - 3 nights ago, the breaker on my EVSE blew immediately after the charge schedule initiated at midnight. In the morning, I tried again - blew within 5 minutes. I didn't have time to debug leading up to NYE so I just charged at public infrastructure until today.

Took a look at the breaker, and the lugs were absolutely loosened up, presumably from heat cycles and time. A quick crank-down and it's been running at full-tilt for the last 30 minutes.

TL;DR - do a once/year checkup on your electrical connections for your EVSE so nothing gets melty.
An add on to that; the lugs reguire a specific torque. Get a good tourqe driver and lookup the required torque value when tightening.
 

CrazyOne

Well-Known Member
Joined
Oct 30, 2021
Threads
3
Messages
1,367
Reaction score
1,162
Location
WA
Vehicles
R1T
PSA - reminder for everyone to do a check-up on your EVSE infrastructure if you've got it at your house.

Some of you will recall I had Mr Melty (electrician used a residential-grade NEMA 14-50 the first time. which subsequently melted in the wall), and the concerns put out by Munroe et. al. regarding breakers frying because of loose connectors or not being rated for continuous 40+ amp draw.

So - 3 nights ago, the breaker on my EVSE blew immediately after the charge schedule initiated at midnight. In the morning, I tried again - blew within 5 minutes. I didn't have time to debug leading up to NYE so I just charged at public infrastructure until today.

Took a look at the breaker, and the lugs were absolutely loosened up, presumably from heat cycles and time. A quick crank-down and it's been running at full-tilt for the last 30 minutes.

TL;DR - do a once/year checkup on your electrical connections for your EVSE so nothing gets melty.
I asked my electrician about 100% duty cycle breakers and he said that they are available only for commercial panels. Mounting the breaker away from others is the best we can do. We can also lower the max charge rate or use an uprated EVSE.

Torquing the connection is a good idea, but I haven't done it.
 
OP
OP
mikehmb

mikehmb

Well-Known Member
First Name
Mike
Joined
Jan 12, 2022
Threads
154
Messages
2,303
Reaction score
5,225
Location
SF Bay Area
Vehicles
My name is Mike, and I have a (car) problem
I asked my electrician about 100% duty cycle breakers and he said that they are available only for commercial panels. Mounting the breaker away from others is the best we can do. We can also lower the max charge rate or use an uprated EVSE.

Torquing the connection is a good idea, but I haven't done it.
For sure. I should clarify in my setup, the EVSE goes to a 50a breaker on a breakout box, then into the main panel on a 100amp breaker shared with another circuit, so in theory the 50a should go first, and the 100 should be good for many years.

In my case, the 100a needed to be re-torqued, and I'll double check the 50a breaker later today after I get charged up.
 

Stevetom84

Well-Known Member
First Name
Stephen
Joined
Jul 11, 2023
Threads
13
Messages
204
Reaction score
205
Location
Atlanta, GA
Vehicles
Rivian R1T
Occupation
Electrical Engineer
For sure. I should clarify in my setup, the EVSE goes to a 50a breaker on a breakout box, then into the main panel on a 100amp breaker shared with another circuit, so in theory the 50a should go first, and the 100 should be good for many years.

In my case, the 100a needed to be re-torqued, and I'll double check the 50a breaker later today after I get charged up.
In theory the 50A should trip before the 100A, but you could go deep in a rabbit hole on breaker coordination. I'm in the electrical field and while not common a higher amperage upstream can trip before a downstream lower amp breaker. Most facilities this isn't an major issue since it's typically nuisance tripping, but in healthcare we have to do the full blow coordination studies to prevent something like a floor cleaning machine tripping an upstream breaker serving an operating room.
 

Sponsored

COdogman

Well-Known Member
First Name
Brian
Joined
Jan 21, 2022
Threads
33
Messages
11,641
Reaction score
34,494
Location
CO
Vehicles
2023 R1T
Occupation
Cyber defender
Clubs
 
Mr. Melty would be a good name for a grilled cheese restaurant.
 

beatle

Well-Known Member
Joined
Jun 20, 2024
Threads
17
Messages
1,148
Reaction score
1,565
Location
Springfield, VA
Vehicles
'23 R1T PDM Max, '97/'25 Miatas, '19 Monkey
Occupation
IT
Clubs
 
Some fasteners need a torque value higher than what that driver tops out at. The EVSE rated Leviton 14-50 recently posted in another thread needs 75 in/lbs.

While it's good to check your breaker and connections, using an IR thermometer can be a quick way to see if Le Résistance is at risk of melting your receptacle or tripping your breaker. Breakers can also trip from high temperature and not just over current. I found once I melted and subsequently replaced my receptacle that the breaker started to trip from the same cause: heat-cycled loose terminal screws.
 

edwjmcgrath

Well-Known Member
First Name
Ed
Joined
Mar 19, 2025
Threads
6
Messages
63
Reaction score
52
Location
Naples
Vehicles
r1s
I'll reinforce this. The power-up self test on our Porsche mobile charger plus threw an error after working fine for several months. I opened it up to torque down the bolts and one of them was stripped. With a little tug the wire came out. This is now the third Hubbell that I've had problems with (although this one could have been an overly aggressive sparky). I know that they are from the same manufacturer, but I'm going with Bryant now.
 

Judd

Active Member
First Name
Judd
Joined
Mar 2, 2025
Threads
0
Messages
43
Reaction score
43
Location
DFW, TX
Vehicles
2023 R1T
When I first got my home setup I charged at 40a and noticed how hot things were getting once summer and the Texas heat started. I checked all the connections and everything was tight, so I backed my charger down to 30a and it made a significant difference. Charging overnite, the lower power time didn’t make that much difference. So I’ve not turned it back up since it’s cooled off.

My point, just because you can…doesn’t always mean we should ;). Great reminder.
 

Sponsored

Meltdwn

Well-Known Member
First Name
Scott
Joined
May 20, 2023
Threads
0
Messages
51
Reaction score
25
Location
Atlanta
Vehicles
R1T LE
Occupation
Business Owner
Based on personal observation, a proper torque wrench is necessary. I used to work on engines and could get very close by feel, when checked with a torque wrench. For fun, I habd torqued my breakers and outlet on install and then with a wrench. I was way under. Bottom line, it’s worth the price to buy a proper range torque wrench and be safe.
I would also make sure a hired electrician does the same.
 

Stevetom84

Well-Known Member
First Name
Stephen
Joined
Jul 11, 2023
Threads
13
Messages
204
Reaction score
205
Location
Atlanta, GA
Vehicles
Rivian R1T
Occupation
Electrical Engineer
When I first got my home setup I charged at 40a and noticed how hot things were getting once summer and the Texas heat started. I checked all the connections and everything was tight, so I backed my charger down to 30a and it made a significant difference. Charging overnite, the lower power time didn’t make that much difference. So I’ve not turned it back up since it’s cooled off.

My point, just because you can…doesn’t always mean we should ;). Great reminder.
We do the exact same thing - keep our EVSE set at 30A for overnight charging. If there is a fault or loose connection simply reducing the amperage won't save you, but reducing heat build up is always good for the longevity of conductor insulation. I tend to put a thermal camera on the breaker and plug every month or so to hopefully catch any potential issues before they become catastrophic.
 

DCFC

Well-Known Member
Joined
Jul 13, 2024
Threads
0
Messages
156
Reaction score
164
Location
SoCal
Vehicles
P2
We do the exact same thing - keep our EVSE set at 30A for overnight charging. If there is a fault or loose connection simply reducing the amperage won't save you, but reducing heat build up is always good for the longevity of conductor insulation. I tend to put a thermal camera on the breaker and plug every month or so to hopefully catch any potential issues before they become catastrophic.
I only charge at as high of a current as required. Heat generation is to the square of current. 40A generates about 78% more heat than 30A. Some nights, I back all the way down to 10A because that's all that is needed to fill up by morning.
 

eRacer

Well-Known Member
First Name
Eric
Joined
Mar 20, 2023
Threads
4
Messages
197
Reaction score
228
Location
Napa, CA
Vehicles
Rivian R1T
Just a PSA about resetting breakers. As an engineer, it's almost a cardinal sin to reset a tripped breaker without finding out what tripped the breaker. It's best to investigate what caused the breaker to trip before trying to reset it. The breaker is made to be the "weak link" within the circuit in a electrical fault scenario. You never know if it will still remain that way after resetting it. Don't become a Mr. Melty yourself.
 

Stevetom84

Well-Known Member
First Name
Stephen
Joined
Jul 11, 2023
Threads
13
Messages
204
Reaction score
205
Location
Atlanta, GA
Vehicles
Rivian R1T
Occupation
Electrical Engineer
Just a PSA about resetting breakers. As an engineer, it's almost a cardinal sin to reset a tripped breaker without finding out what tripped the breaker. It's best to investigate what caused the breaker to trip before trying to reset it. The breaker is made to be the "weak link" within the circuit in a electrical fault scenario. You never know if it will still remain that way after resetting it. Don't become a Mr. Melty yourself.
Good advice for any breaker that trips out of the blue, not just your EVSE.