- Thread starter
- #1
I’ve been using a Tesla Universal Wall Charger to charge my Model Y and R1S for almost 2 years.
The install was coordinated by Qmerit and the electrician they contracted knew what they were doing. My neighbor also used them and would concur.
Recently I noticed that the R1S was only charging at 24 amps. This charger is on a 60-amp breaker and set to charge at 48amps.
Historically both vehicles always charged at 48 amps, there always has been some minor humming and warming of the conduit, but never what I would consider to be “hot” to the touch. Just warm. I was told this is normal.
I am able to replicate this event. Set the charging rate in the R1S to 48 amps. Start charging. Wait 10-15-20 minutes, then the charging rate drops to 24 amps.
I do not see this behavior with the Tesla.
If I set the R1S to charge at 40 amps instead of 48 amps (1) the charging rate remains at 40 amps without derating (2) there is no electrical humming and (3) the electrical conduit does not heat up.
Does anyone have any troubleshooting tips on steps I can take to determine the cause of the derating when trying to charge at 48 amps?
The install was coordinated by Qmerit and the electrician they contracted knew what they were doing. My neighbor also used them and would concur.
Recently I noticed that the R1S was only charging at 24 amps. This charger is on a 60-amp breaker and set to charge at 48amps.
Historically both vehicles always charged at 48 amps, there always has been some minor humming and warming of the conduit, but never what I would consider to be “hot” to the touch. Just warm. I was told this is normal.
I am able to replicate this event. Set the charging rate in the R1S to 48 amps. Start charging. Wait 10-15-20 minutes, then the charging rate drops to 24 amps.
I do not see this behavior with the Tesla.
If I set the R1S to charge at 40 amps instead of 48 amps (1) the charging rate remains at 40 amps without derating (2) there is no electrical humming and (3) the electrical conduit does not heat up.
Does anyone have any troubleshooting tips on steps I can take to determine the cause of the derating when trying to charge at 48 amps?