Yes, he should flip dip switch 3 to OFF if the wire gets too warm.The round up rule is for sizing the breaker not the wire. If you had a 44A continuous load, you could use 55A wire with a 60A breaker. This install is a 48A continuous load, requiring 60A ampacity for the wire. That's the code.
The wires inside a romex cable, however, are 90C THHN wires. The code requirement to not exceed the 60C ampacity does seem a little arbitrary (though I'm sure it's there for good reason). The romex install will most likely be fine from a safety point of view, but it isn't technically up to code. And I second @ajdelange in wanting to make sure readers who may be pursuing their own installs are aware of the code. If somebody decides to do it anyways fully understanding the decision they're making, that doesn't bother me at all.