So, a couple of things here, not to argue but just trying to understand and clarify.
The article referenced addresses amperage drop over a long run. Nicely explained, however the example given is "to deliver 60 amps to a service panel ". We are not trying to *deliver* 60 amps.
In my situation, and perhaps your's, I am attempting to deliver 48 amps to an EVSE on a 100 ft or less branch circuit. No more, no less, notwithstanding future proofing.
Using the 80% rule, (if I understand it correctly) I need to size my conductor at 57.6 amps for a 100 foot run , and/or 62.4 for a 150 ft run.
I would think a 60 amp breaker with a 6 AWG THHN in a conduit or 6 AWG MC would be sufficient to supply an EVSE at 100 feet safely.
The article referenced addresses amperage drop over a long run. Nicely explained, however the example given is "to deliver 60 amps to a service panel ". We are not trying to *deliver* 60 amps.
In my situation, and perhaps your's, I am attempting to deliver 48 amps to an EVSE on a 100 ft or less branch circuit. No more, no less, notwithstanding future proofing.
Using the 80% rule, (if I understand it correctly) I need to size my conductor at 57.6 amps for a 100 foot run , and/or 62.4 for a 150 ft run.
I would think a 60 amp breaker with a 6 AWG THHN in a conduit or 6 AWG MC would be sufficient to supply an EVSE at 100 feet safely.