Hardwired only (likely to meet NEC requirements)

As a plug-in, it would not meet the requirement prohibiting adjustable amperages, and is not set up for tool free removal (also required).

They did comply with the requirement for restricted access to the amperage settings (dip switches in this case).
 

jjswan33

Well-Known Member
First Name
Joshua
Joined
Sep 17, 2021
Messages
105
Reaction score
163
Location
Sandy, OR
First Name
Joshua
Vehicles
Ram Promaster
Occupation
Engineer
Interesting that they suggest 6 awg wire is sufficient for the full 60A circuit setting, I guess since it only pulls 48A that is ok? I was under the impression that a 60A circuit would need 4 awg wiring.
 

kommonplace

Well-Known Member
First Name
Kevin
Joined
May 31, 2021
Messages
68
Reaction score
235
Location
Bardstown, KY, USA
Website
www.kevinjwangler.com
First Name
Kevin
Vehicles
2014 Ford Flex, non-LE R1S preorder
Occupation
IT Director
How easy would it be to replace a Tesla Wall Charger (hardwired) with one of these guys? For someone who typically doesn't mess with electricity.
 

kommonplace

Well-Known Member
First Name
Kevin
Joined
May 31, 2021
Messages
68
Reaction score
235
Location
Bardstown, KY, USA
Website
www.kevinjwangler.com
First Name
Kevin
Vehicles
2014 Ford Flex, non-LE R1S preorder
Occupation
IT Director
easy peezy as long as you know how to turn off your circuit breaker.
Now THAT I can do! I read the guide (honestly, Rivian could publish just about any piece of information and I'd read it) and it looked.... very easy. Just wanted to make sure it was as easy as it looked. Thank you!
 

SANZC02

Well-Known Member
First Name
Bob
Joined
Feb 11, 2021
Messages
880
Reaction score
1,821
Location
California
First Name
Bob
Vehicles
Tesla Model S, Jeep Grand Cherokee; (LE - R1S)
Occupation
IT
How easy would it be to replace a Tesla Wall Charger (hardwired) with one of these guys? For someone who typically doesn't mess with electricity.
Not difficult but if you are not familiar with doing electrical fixtures may not want to start here.

With the amount of amps being pulled if the wires are not seated and torqued properly they could generate excessive heat. You also have to look at the wires and breakers installed to ensure you set the dip switches for the proper draw.
 

DucRider

Well-Known Member
First Name
Gary
Joined
Oct 21, 2019
Messages
1,628
Reaction score
2,942
Location
rRegon
First Name
Gary
Vehicles
Clarity Electric
Interesting that they suggest 6 awg wire is sufficient for the full 60A circuit setting, I guess since it only pulls 48A that is ok? I was under the impression that a 60A circuit would need 4 awg wiring.
6 awg is fine as long as it is 90° rated
If thinking of using NM-B (Romex), it is not OK as it requires using the 60° column/rating
 

kommonplace

Well-Known Member
First Name
Kevin
Joined
May 31, 2021
Messages
68
Reaction score
235
Location
Bardstown, KY, USA
Website
www.kevinjwangler.com
First Name
Kevin
Vehicles
2014 Ford Flex, non-LE R1S preorder
Occupation
IT Director
Not difficult but if you are not familiar with doing electrical fixtures may not want to start here.

With the amount of amps being pulled if the wires are not seated and torqued properly they could generate excessive heat. You also have to look at the wires and breakers installed to ensure you set the dip switches for the proper draw.
It's a 60A breaker so I believe I'd be leaving it at the default settings on the dip switches.

The torque part, I had planned on "okay, that feels tight enough" but your comment is making me think that is not going to cut it. My wife said "get whatever you need" ... until we saw the prices on those guys. Sheesh. No wonder I don't own one!

Thanks for your reply—very helpful.
 

lefkonj

Well-Known Member
First Name
Jeff
Joined
Feb 6, 2021
Messages
50
Reaction score
64
Location
New Jersey
First Name
Jeff
Vehicles
A7/Q3 R1S ordered
I thought their charger was Nema 14-50 or Hardwired. These docs say hardwired only or am I wrong? That sucks
 

timesinks

Well-Known Member
Joined
Sep 20, 2020
Messages
190
Reaction score
407
Location
Seattle
Vehicles
ID.4, FJ, Sprinter
I thought their charger was Nema 14-50 or Hardwired. These docs say hardwired only or am I wrong? That sucks
The portable one that comes with the vehicle will be plug and cord. The wall charger will be hardwire.
 

Amy

New Member
First Name
Amy
Joined
Aug 24, 2021
Messages
2
Reaction score
2
Location
Dallas,TX
First Name
Amy
Vehicles
Mazda CX5
How easy would it be to replace a Tesla Wall Charger (hardwired) with one of these guys? For someone who typically doesn't mess with electricity.
Like said before, do not start here. High Amps can be a major fire hazard if you don't tighten thing down and strip wires wrong.
 

Ssaehrig

Member
First Name
Steven
Joined
Aug 17, 2021
Messages
11
Reaction score
13
Location
CT
First Name
Steven
Vehicles
2018 Durango SRT, 2013 GMC Acadia
Occupation
IT Executive
Interesting that they suggest 6 awg wire is sufficient for the full 60A circuit setting, I guess since it only pulls 48A that is ok? I was under the impression that a 60A circuit would need 4 awg wiring.
I am going with the higher capacity wire. No need to stress the wiring.
 