I apologize if I came across too harshly. It’s just that I get so tired of people on EV forums throwing out careless electrical advice.First, I said "at least 6AWG copper wiring."
Like you pointed out, changing breakers is easy, but it ignores the fact that you should do a quick load calculation to be certain you’re not overloading your circuit breaker panel. Adding a 70-amp breaker to a 100-amp or even a loaded 200-amp panel is not wise. For example, there are situations where you may have to swap an electric water heater out for a gas heater in order to make room for an EV charger. You should point out these caveats anytime you recommend adding breakers to a panel.
And, as you also pointed out, you advised the OP to use at least 6 AWG, but you failed to add that only 6 AWG THHN copper wire can handle 70 amps and that it must be run in conduit. You run the risk of some DIY’er going to Lowes, seeing NM-B wire and assuming 6 AWG is good enough. Again, you should point out the caveats of your recommendations.
It’s nice that you jump into these threads to help out, but please give some thought to the advice that you offer.